Re: 277/480 Volt Panel
Please clarify one thing for me. I think you are saying that the ?distribution panel? has a 400 amp fuse that protects the feeder to the ?new? 400 amp panel. If that is the case, then the new panel can be MLO.
But you might be saying that 400 amp fuse is the main overcurrent device that protects the distribution panel itself, and you might be giving us no information about any device that protects the feeder to the new panel. If this is the case, then you need to describe the method of connection between the distribution panel and the new panel.