Re: 277/480
Renosteinke is right. In addition, both 277 and 480 will have the same class of insulation (i.e., 600V). So neither will impose a threat to the other. Here?s what I mean: A major reason that we don?t (for example) put a 4160V cable alongside a 480V cable is that a breakdown of the 4kV cable?s insulation might impose every bit of 4160V on the 480V cable?s insulation, and it could not take that stress. Two cables of the same voltage class would not have this concern.