277 v. vanity mirror lighting

Status
Not open for further replies.

jzups

Member
I am working on a project where we have installed 277volt lights to back light several mirrors located at sinks in a locker room. The light fixtures are behind the mirrors and someone standing at the sink could eaisly place their hand behind the mirror and come in contact with the light fixture. The e.e.on the project says all we need to do is put a plastic lens over the opening to prevent contact with the fixture which is only 8 inches above the sink. I say we need GFCI protection and a lens,although I was told there is no 277v .GFCI breaker available for the panels we have on the project. Am I right or wrong ?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
jzups said:
I am working on a project where we have installed 277volt lights to back light several mirrors located at sinks in a locker room. The light fixtures are behind the mirrors and someone standing at the sink could eaisly place their hand behind the mirror and come in contact with the light fixture. The e.e.on the project says all we need to do is put a plastic lens over the opening to prevent contact with the fixture which is only 8 inches above the sink. I say we need GFCI protection and a lens,although I was told there is no 277v .GFCI breaker available for the panels we have on the project. Am I right or wrong ?

What is your code reference for GFCI protection on any vanity light???
 

haskindm

Senior Member
Location
Maryland
For the most part only RECEPTACLES in Bathrooms require GFCI protection. No receptacle = no GFCI. There is something about a light over a tub needing GFCI in some cases but I don't have an NEC to look it up right now and it would not appy to this installation.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
haskindm said:
For the most part only RECEPTACLES in Bathrooms require GFCI protection. No receptacle = no GFCI. There is something about a light over a tub needing GFCI in some cases but I don't have an NEC to look it up right now and it would not appy to this installation.

There is no GFCI required for a light over a tub, however there are manufacturers instructions that require GFCI protection when the fan is installed over a shower area. I have never seen a light that requires GFCI for a bath--- The nec does not require it but does have other requirement for lights over tubs, etc. 410.4(D) 2005
 

haskindm

Senior Member
Location
Maryland
Pehaps it was the fan I was remembering. Thanks. The impoirtant thing to remember is that, in almost all cases, GFCI is only required for receptacles. The list of hard-wired equipment that requires GFCI protection is VERY short.
 
Status
Not open for further replies.
Top