277 Volt Lighting Mounting Heights

Status
Not open for further replies.

John Trippel

New member
I have a NEC Code Question that I have not been able to find an answer for in the code. What is the minimum allowable mounting height for 277 volt lighting and where is this found in the code? The installation is for industrial and commercial applications.

[ February 03, 2006, 09:00 AM: Message edited by: John Trippel ]
 
Re: 277 Volt Lighting Mounting Heights

There is not a minimum height for 277V luminaires, how ever there is for over 277V.

See 210.6(D)

Roger
 
Re: 277 Volt Lighting Mounting Heights

Several years ago, like maybe 1981 NEC or so, there were some minimum height restrictions on 277V. ltg., but believe roger is correct.
 