kevinware
- Louisville, KY
Last night in my electrical class my instructor stated that in a 480/277v lighting system it was an NEC violation to use a white wire as a neutral and that I was suppose to use a gray wire all the way to the fixture. I understand the use of brown, orange, yellow for the courtesy factor. But I looked all through article 200 and all I find is the reference to the use of white or gray conductor.
200.6(A)
An insulated grounded conductor of 6 AWG or smaller shall be identified by a continuous white or gray outer finish or by three continuous white stripes on other than green insulation along its entire length.
I only see a change when I come to 200.6(D)
Where conductors of different systems are installed in the same raceway, cable, box, auxiliary gutter, or other type of enclosure, one system grounded conductor, if required, shall have an outer covering conforming to 200.6(A) or 200.6(B). Each other system grounded conductor shall have an outer covering of white with a readily distinguishable , different colored stripe other than green running along the insulation, or shall have other different means of identification as allowed by 200.6(A) or 200.6(B) that will distinguish each system grounded conductor.
So if I use a white conductor, not a gray conductor, as my neutral in a 480/277V lighting system is that an NEC violation or is it a courtesy violation???????
Thanks for all your help, I learn so much from this site.
Kevin
[ March 29, 2005, 12:20 PM: Message edited by: kevinware ]
200.6(A)
Kevin