tx2step
Senior Member
- Location
- North Texas, DFW area
There will be 2 ea. 277V switchlegs + 1 ea. 120V switchleg in the same 3-gang switchbox. If the 277V switchlegs are on different phases, 404.8(B) requires a barrier (divider) between the 277V switches.
But what about the 120V switch? Does it need a barrier/divider as well?
The commentary following 404.8(B) in the NEC handbook says (in part): "...This requirement also applies to switches ganged together with any wiring device where the voltage between adjacent conductors exceeds 300-volts. Where switches or devices are on different systems and are in the same box, such as a switch on a 277-volt system and a receptacle on a 120-volt system, a careful analysis of the voltage between adjacent device terminals is required to ensure that the 300-volt limitation is not exceeded."
So with 277V and 120V switchlegs in the same switch box, what are the conditions that would create 300V or more between wires/terminals?
I usually don't mix the 2 voltages in device boxes for fear of accidentally imposing 277V onto 120V wiring...which I would think would be bad for any connected devices. So I haven't run into an occasion before where the 2 voltages will be present in the same switchbox.
Are "...identified, securely installed barriers..." required between the 277V and 120V wiring/devices? by "identified" I assume they must be "listed" for that use?
But what about the 120V switch? Does it need a barrier/divider as well?
The commentary following 404.8(B) in the NEC handbook says (in part): "...This requirement also applies to switches ganged together with any wiring device where the voltage between adjacent conductors exceeds 300-volts. Where switches or devices are on different systems and are in the same box, such as a switch on a 277-volt system and a receptacle on a 120-volt system, a careful analysis of the voltage between adjacent device terminals is required to ensure that the 300-volt limitation is not exceeded."
So with 277V and 120V switchlegs in the same switch box, what are the conditions that would create 300V or more between wires/terminals?
I usually don't mix the 2 voltages in device boxes for fear of accidentally imposing 277V onto 120V wiring...which I would think would be bad for any connected devices. So I haven't run into an occasion before where the 2 voltages will be present in the same switchbox.
Are "...identified, securely installed barriers..." required between the 277V and 120V wiring/devices? by "identified" I assume they must be "listed" for that use?