Will you have 277 volt loads? If so you will need the 480/277 (which is a wye secondary) or else separately derive it on site, but given choice up front you are better off getting what you need.
If you have limited load application, for example a pumping station, you may be more likely to desire the 480 volt three wire system (which is from a delta secondary).
Note that using typical 277/480 volt panelboards such as Square D's NF panels - they can't be used on a 480 volt delta, those breakers are 277/480 rated and can not be used when there is more than 277 nominal to ground, which means you need higher rated panels such as I-Line or use fuses witch is also more common for limited load applications.