277v and 120v device without barrier.

darekelec

Senior Member
Location
nyc
Will I get 380V difference in potential between devices every time or is there a phase combination that barrier will not be necessary?

Meaning if I choose corresponding windings of a transformer the voltage will be less than 150V between devices and no barrier is required.

Thank you.
 

Attachments

  • IMG_3895.jpeg
    IMG_3895.jpeg
    770.5 KB · Views: 11
With a delta-wye transformer, the phase angle between a 120V L-N and a 277V L-N will be 30 degrees, 150 degrees, or 270 degrees (-90 degrees).

So the voltage between the two ungrounded conductors will be 183V, 385V, or 301V.

Cheers, Wayne
 
Voltage diffrence between devices should not exceed 300v (not 150V as I wrote in opening statement) so there is a combination of phases that would not mandate me to install a barrier.
Thank you
 