277V GFI protection required

Status
Not open for further replies.

amsmith

New member
The inspector on one of our jobs that is about to end is now requiring GFCI protection to a 277 Volt lightinging circuit around a pool.
A 277V Pass though GFI does not exist nor does a 277V GFI breaker. Any suggestions short of bringing in a 120 V circuit?:-?
 
art. 680.22 makes no mention of voltage. Seems like some designer screwed up here. Sounds like a change out to 120V is the solution.
 