277V lighting in bathroom

Status
Not open for further replies.

bonding jumper

Senior Member
Are their any provisions, restrictions against doing this? This is a commercial bathroom for an office. The fixtures are to be installed recessed in the ceiling above the sink, and I was wondering because I am new with 277, if there were any provisions. I missed the one that stated that undercounter lighting must be 120 because it is not a certain distance from the floor, so I was just checking if I was missing any other provisions. Thanks in advance.
 
Re: 277V lighting in bathroom

We do that all the time in commecial building if there is 277 available. there is no restriction in code against doing that.
 
Re: 277V lighting in bathroom

Not that its likely to change your design, but you might check 210.6(C).
 
Re: 277V lighting in bathroom

Originally posted by bonding jumper:
...I missed the one that stated that undercounter lighting must be 120 because it is not a certain distance from the floor....
What do you mean by this? :confused:
 