(C) 277 Volts to Ground. Circuits exceeding 120 volts,
nominal, between conductors and not exceeding 277 volts,
nominal, to ground shall be permitted to supply the following:
(1) Listed electric-discharge or listed light-emitting diodetype
luminaires
(2) Listed incandescent luminaires, where supplied at
120 volts or less from the output of a stepdown autotransformer
that is an integral component of the
luminaire and the outer shell terminal is electrically
connected to a grounded conductor of the branch
circuit
(3) Luminaires equipped with mogul-base screw shell lampholders
(4) Lampholders, other than the screw shell type, applied
within their voltage ratings
(5) Auxiliary equipment of electric-discharge lamps
(6) Cord-and-plug-connected or permanently connected
utilization equipment