277volt and 480volt wiring without a neutral

Status
Not open for further replies.

mikebourland

Member
Location
hammond,IN
All,

I have a question regarding 3 phase power without the use of a neutral. I received a question asking if it is proper to wire a 480v parking lot light using only 2 hot conductors (=480v single phase?) and a ground. The other hot leg and neutral are going elsewhere in the facility so a neutral is not available.

In general, I am unsure when a neutral is needed and when it is not. I know there are 3 phase wiring systems that do not have a neutral at all. I think they work off the principal that while 1 phase is providing power, another phase is handling the return voltage.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
All,

I have a question regarding 3 phase power without the use of a neutral. I received a question asking if it is proper to wire a 480v parking lot light using only 2 hot conductors (=480v single phase?) and a ground. The other hot leg and neutral are going elsewhere in the facility so a neutral is not available.

In general, I am unsure when a neutral is needed and when it is not. I know there are 3 phase wiring systems that do not have a neutral at all. I think they work off the principal that while 1 phase is providing power, another phase is handling the return voltage.

480V phase to phase for a light is basically the same as 240V for your water heater.

Technically speaking you don't "need" a neutral ever to make something work and there are some specific rules about how the grounded/neutral conductor is treated, but there's nothing magical about it, it's just another circuit conductor.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The difference is, you will need a 2 pole circuit breaker for the 480V feed, vs a 1 pole breaker for a 277V feed. Same number of conductors of course, but you take up more space in your panelboard.
 

mikebourland

Member
Location
hammond,IN
Welcome, and it's commonly done that way.

The neutral/ground bond must be done.

Heres the issue. Currently to this outside light, there is a single phase 480 system and a ground wire. Someone ordered a replacement light that operates at 277v. Would it be possible to use 1 leg from the 480 which is 277 and for the return use the ground conductor? Ive always been told that the ground circuit shouldnt be used as a common return, only for safety purposes only. So the question is, can I use 277 leg and a ground to power outside light? Id think no, but would like advice from yous. Thank you.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
...... So the question is, can I use 277 leg and a ground to power outside light? Id think no, but would like advice from yous. Thank you.

Absolutely no. What you are calling a ground is more properly called an equipment grounding conductor, and as you've been told, it is there for the purpose of clearing a fault only.

You can pull new wire, you may even be able to re purpose one of the existing hot conductors, even better, just get a light that works on the voltage you have already.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Seriously? Using the EGC as a neutral? I didn't think that was ever OK.
No, I meant it's common to supply a load with two line conductors and no grounded conductor.

Read the OP and the question I was answering; no mention of using the EGC as a circuit conductor.
 