Hi,
can I use the neutral of 480/277v system
in 120v circuit feeding 120v loads????
tanx
can I use the neutral of 480/277v system
in 120v circuit feeding 120v loads????
tanx
Hi,
can I use the neutral of 480/277v system
in 120v circuit feeding 120v loads????
tanx
NEC won't allow it, but POCO's do that all the time with a common neutral for primary and secondary distribution.
This is a good question...... What if the 480/277 neutral is bonded to a great ufer ground?? Technically it should be ok but code wise is different.
Normally the 120V trafo is a separately derived entity. The primary, if single phase, will be 2 wire only 480V (with no neutral). The secondary will be 240/120 split phase and the ufer ground will be the neutral. It will also be the ground.
If a 3 phase is used the trafo primary will be a delta (so 3 wires, no neut) and the secondary will be 3 phases of 240/120 split phase The ufer ground will be the neutral. It will also be the ground for all the metal.
I say ufer ground since I do not trust most other grounds.
This is a good question...... What if the 480/277 neutral is bonded to a great ufer ground?? Technically it should be ok but code wise is different.
Normally the 120V trafo is a separately derived entity. The primary, if single phase, will be 2 wire only 480V (with no neutral). The secondary will be 240/120 split phase and the ufer ground will be the neutral. It will also be the ground.
If a 3 phase is used the trafo primary will be a delta (so 3 wires, no neut) and the secondary will be 3 phases of 240/120 split phase The ufer ground will be the neutral. It will also be the ground for all the metal.
I say ufer ground since I do not trust most other grounds.
What does that mean? You can't have three 240/120 split phase from a single three phase transformer with center tapped secondary coils, can you? The center taps would all be at different potentials from each other; you can't tie them together.If a 3 phase is used the trafo primary will be a delta (so 3 wires, no neut) and the secondary will be 3 phases of 240/120 split phase delta.
What does that mean? You can't have three 240/120 split phase from a single three phase transformer with center tapped secondary coils, can you? The center taps would all be at different potentials from each other; you can't tie them together.
That is true, and with the MGN system they have they don't use EGC's but there is a GEC to every electrode used and some current does pass through those electrodes, most of it likely being current associated with the meduim voltage system more so then low voltage systems.Not a just a common neutral, a multigrounded neutral.
I don't see that as the same thing as having using EGCs and GECs as circuit conductors.