There are 50 hanging fixtures all 277-volt with 200watt incandescent lamps (there is a large acrylic diffuser with a porcelain lamp holder - like a low bay fixture retrofitted with a lamp holder and incandescent lamp). The new lamps started burning out at a pretty rapid pace. I checked voltage at the fixture and got 284 volts. I check at the breaker and got 284 volts. I check at the line side coming in from the utility service and got 284 volts. I called the manufacturer of the lamp and they confirmed that anything over 277 volts would cause the lamp to overheat and ultimately malfunction. Is it possible that the utility company is supplying too much voltage from the transformer? Is is pretty common for the voltage to be that much higher than what it is supposed to be? Is there any solution? Im confused....