2HR Rated Wire

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
So RHH/RHW-2 is the same cable(dual rating) sort of like THHN/THWN?
Thanks.........................
 

Attachments

  • VitalinkRHWUSMarket37711.pdf
    77 KB · Views: 12

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes. Are you using this for a fire pump in EMT? That stuff is horrible to pull in a raceway.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You might find some with only one rating but most is RHH-RHW-2 and often USE-2 added
Simplified manufacturing and warehousing.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
The OP needs to be aware that if he is trying to achieve a 2 hour fire rating with this there is more to it that just simply installing this in EMT as there are all kinds of requirements for how the raceway is installed. In other words, it has to to be installed as a "system" complying with UL FHIT.
 