hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
This is going to be a little long so bear with me
Last month I had the GFP trip out a 2k amp breaker on a ground fault in a large theater with 15 screens and 1 I-Max.
This cause the theaters to go dark which freaked a few people out so state FM got called and I was called in to find out why the Emg lights didn't respond, ok here's what I found.
The breaker that tripped is on a 208/120 MDP fed from a 750kva transformer fed from a 900amp breaker in the 480/277 MDP main service with a 2k amp GFP main breaker also.
one of the first things noted is all the Emg lights are fed from the 277 volt systems so this was the reason why they didn't respond to the 208/120 going down, but when a movie is playing, each theater is lighted by LV runway lights from small transformers on the 120/208 system, and wall sconce's and cans up in the ceiling are on a dimmer pack controlled by the projector computers also fed from the 120/208 system.
So I pondered about 3 alternatives to light the theaters in the event of the loss of the 208 system:
1 install UPS systems on the LV lighting and cans in each projector room.
2 re-supply the Emg lights from the 120/208 system
3 shunt trip out the 277/480 from the 120/208 system
Bet you can guess which one they chose to do
Yep shunt trip it is.
the first two being that this complex is so vast and large the cost was quite high.
Bad thing was option 2 at the time of install would have not cost anything extra if someone would have caught it!!!!
To touch on why the GFP tripped was because someone thought doing the panel coordination study and setting the GFP on the 277/480v main was enough and left the GFP on the 120/208 set to the low factory settings which left the main set to 150amps GFP, a line to ground fault in a cord to a popcorn machine caused the ground fault that was on a 2-pole 50 amp breaker, in a 225 amp sub-panel fed from the 120/208v MDP, nether the 2-pole 50 or the 225 amp breaker tripped which is what led me to look at the GFP settings.
They had a panel coordination study done and the GFP properly set.
We had them get a GE engineer out to assist in figuring out a way to trip the 277/480 main out from the 120/208 system, well this is where it all went down hill, with out looking the GE EE assumed the power break main had the modules in them and the auxiliary contacts installed in them, so they had us order a shunt trip module, and a under voltage module, alarm bell module.
All sounded right, as I had no idea as to how the under voltage module worked in a GE system assuming it monitored all 3 phase and would have a dry contact to trip the shunt trip breaker, at least this is what I thought???
Nope not this thing, it requires a 24 volt DC control voltage to be supplied to its two terminals, ok called GE tech and asked where do I get this from, they replied from the 120/208 system via a 24 volt power supply, Oh and get this the UVR goes into the 277/480 main because when the 24vdc drops below 60% it trips out the main
Ok so I said let me get this straight when the 120/208 loses power the power supply loses power and this UVR trip the main in the 277/480 system right, he said yep, ok so to power back up the 277/480 main I just charge it and turn it back on and the UVR resets, (this is where it get interesting) he says no, I have to have 24vdc applied to the UVR before I can reset the main on the 277/480??? I ask him now since the 480 in down where do I get 24vdc from??
he tells me from the 208 system, I ask how since it is supplied from the 480 system, the phone went dead quiet after a few another GE EE gets on, and I go through the whole story again,
Finely I just asked them if the shunt trip will trip the 480 main if I apply a 24 vac to it, and he said yes, so I said no problem I'll get it done TY and good bye.
So I drew up a little diagram for a couple relays and a transformer and it worked flawlessly, now I hope it passes state
The attached diagram is simple:
a 100va 277/24 v transformer supplies the trip control power, relay 1 normally closed contact is the 120/208 monitor to signal the 480 main to trip, the time delay on is used to prevent false trips during normal power failures by opening the 24 volts to the trip circuit for 3 seconds, and allow resetting the system after a 120/208 loss trip out, of course the breaker supplying the transformer will have to be shut off till the 120/208 main is reset, but this was the simplest way I could see to do this job?
For discussion:
1 Has anyone else ran into an oversight such as this?
2 does anyone else know of a simpler circuit or a change to mine that would not require the breaker feeding the transformer or 24 volt supply to be shut down till the 208 is brought back up? remember the 120/208 is fed from the 277/480?
3 Has anyone else had these kind of problems dealing with GE engineers?
$ how do you recover the $480 when I try to return the UVR to the supply house when this was a miss ordered item caused by a request from GE them selves??? they are going to want a re-stock fee?? should I tell them to get it from GE?
Ya I got frustrated over this one.
Last month I had the GFP trip out a 2k amp breaker on a ground fault in a large theater with 15 screens and 1 I-Max.
This cause the theaters to go dark which freaked a few people out so state FM got called and I was called in to find out why the Emg lights didn't respond, ok here's what I found.
The breaker that tripped is on a 208/120 MDP fed from a 750kva transformer fed from a 900amp breaker in the 480/277 MDP main service with a 2k amp GFP main breaker also.
one of the first things noted is all the Emg lights are fed from the 277 volt systems so this was the reason why they didn't respond to the 208/120 going down, but when a movie is playing, each theater is lighted by LV runway lights from small transformers on the 120/208 system, and wall sconce's and cans up in the ceiling are on a dimmer pack controlled by the projector computers also fed from the 120/208 system.
So I pondered about 3 alternatives to light the theaters in the event of the loss of the 208 system:
1 install UPS systems on the LV lighting and cans in each projector room.
2 re-supply the Emg lights from the 120/208 system
3 shunt trip out the 277/480 from the 120/208 system
Bet you can guess which one they chose to do
Yep shunt trip it is.
the first two being that this complex is so vast and large the cost was quite high.
Bad thing was option 2 at the time of install would have not cost anything extra if someone would have caught it!!!!
To touch on why the GFP tripped was because someone thought doing the panel coordination study and setting the GFP on the 277/480v main was enough and left the GFP on the 120/208 set to the low factory settings which left the main set to 150amps GFP, a line to ground fault in a cord to a popcorn machine caused the ground fault that was on a 2-pole 50 amp breaker, in a 225 amp sub-panel fed from the 120/208v MDP, nether the 2-pole 50 or the 225 amp breaker tripped which is what led me to look at the GFP settings.
They had a panel coordination study done and the GFP properly set.
We had them get a GE engineer out to assist in figuring out a way to trip the 277/480 main out from the 120/208 system, well this is where it all went down hill, with out looking the GE EE assumed the power break main had the modules in them and the auxiliary contacts installed in them, so they had us order a shunt trip module, and a under voltage module, alarm bell module.
All sounded right, as I had no idea as to how the under voltage module worked in a GE system assuming it monitored all 3 phase and would have a dry contact to trip the shunt trip breaker, at least this is what I thought???
Nope not this thing, it requires a 24 volt DC control voltage to be supplied to its two terminals, ok called GE tech and asked where do I get this from, they replied from the 120/208 system via a 24 volt power supply, Oh and get this the UVR goes into the 277/480 main because when the 24vdc drops below 60% it trips out the main
Ok so I said let me get this straight when the 120/208 loses power the power supply loses power and this UVR trip the main in the 277/480 system right, he said yep, ok so to power back up the 277/480 main I just charge it and turn it back on and the UVR resets, (this is where it get interesting) he says no, I have to have 24vdc applied to the UVR before I can reset the main on the 277/480??? I ask him now since the 480 in down where do I get 24vdc from??
he tells me from the 208 system, I ask how since it is supplied from the 480 system, the phone went dead quiet after a few another GE EE gets on, and I go through the whole story again,
Finely I just asked them if the shunt trip will trip the 480 main if I apply a 24 vac to it, and he said yes, so I said no problem I'll get it done TY and good bye.
So I drew up a little diagram for a couple relays and a transformer and it worked flawlessly, now I hope it passes state
The attached diagram is simple:
a 100va 277/24 v transformer supplies the trip control power, relay 1 normally closed contact is the 120/208 monitor to signal the 480 main to trip, the time delay on is used to prevent false trips during normal power failures by opening the 24 volts to the trip circuit for 3 seconds, and allow resetting the system after a 120/208 loss trip out, of course the breaker supplying the transformer will have to be shut off till the 120/208 main is reset, but this was the simplest way I could see to do this job?
For discussion:
1 Has anyone else ran into an oversight such as this?
2 does anyone else know of a simpler circuit or a change to mine that would not require the breaker feeding the transformer or 24 volt supply to be shut down till the 208 is brought back up? remember the 120/208 is fed from the 277/480?
3 Has anyone else had these kind of problems dealing with GE engineers?
$ how do you recover the $480 when I try to return the UVR to the supply house when this was a miss ordered item caused by a request from GE them selves??? they are going to want a re-stock fee?? should I tell them to get it from GE?
Ya I got frustrated over this one.