Any feedback why I should use 2P disconnect switch instead of 1P disconnect switch for single pole 220v loads?
 
Not sure what voltage system you are working with(Cairo) but , in most cases, such as 422,.31 &b 430.103, it is required that the disconnect open all ungrounded conductors on on US stystems it is required so as to reemove shock hazard from voltage to ground....
 
Not sure what voltage system you are working with(Cairo) but , in most cases, such as 422,.31 &b 430.103, it is required that the disconnect open all ungrounded conductors on on US stystems it is required so as to reemove shock hazard from voltage to ground....
2P means ungrounded + neutral on 3ph 400v/1ph 220v system,

IMHO, I cannot see a real reason for having 2P disconnect switch in such systems
 