Say the standard hot tub panel with no 120V receptacle, just the 240V to the spa.
I run 4 wire cable to the hot tub box, so that the client can test the GFCI. It won't trip with the test button without a neutral.
But, will a 2P breaker trip without a neutral in a real life ground fault situation? Will the breaker read an imbalance between 2 hots? What if there is no 120V loads? Just 240V off the breaker?
I haven't had the opportunity to put the Lo-Z meter on it and see what happens.
I run 4 wire cable to the hot tub box, so that the client can test the GFCI. It won't trip with the test button without a neutral.
But, will a 2P breaker trip without a neutral in a real life ground fault situation? Will the breaker read an imbalance between 2 hots? What if there is no 120V loads? Just 240V off the breaker?
I haven't had the opportunity to put the Lo-Z meter on it and see what happens.