I recently installed a Eaton BR 2P30 GFCI circuit breaker in my clients sub panel for a duel fuel range that was being installed. The circuit breaker began tripping for no apparent reason overnight when the stove was never being used.
Had the customer unplug the range before bed to confirm and sure enough the circuit tripped again overnight. (this is a direct 30a line with nothing else on the circuit)
After this happened I figured it was a problem with the wiring and by now I would have just run a new wire if there wasnt going to be so much drywall work involved.
Went back to troubleshoot and couldn't re create the problem so out of curiosity I put in another Eaton BR 2P30 GFCI with no wires going to it (just the pigtail going to neutral bar).
Sure enough that circuit breaker tripped last night too (not at the same time as the range circuit breaker but before)
Reaching out to see if anyone has had this problem before and how they solved it. I've always been good at troubleshooting but this is a first for me.
Had the customer unplug the range before bed to confirm and sure enough the circuit tripped again overnight. (this is a direct 30a line with nothing else on the circuit)
After this happened I figured it was a problem with the wiring and by now I would have just run a new wire if there wasnt going to be so much drywall work involved.
Went back to troubleshoot and couldn't re create the problem so out of curiosity I put in another Eaton BR 2P30 GFCI with no wires going to it (just the pigtail going to neutral bar).
Sure enough that circuit breaker tripped last night too (not at the same time as the range circuit breaker but before)
Reaching out to see if anyone has had this problem before and how they solved it. I've always been good at troubleshooting but this is a first for me.
- Grounds and neutrals separated in sub panel
- Already replaced with another circuit breaker and it did the same thing
- These circuit breakers also have trip codes and it is showing 4 white blinks (meaning it is a ground fault above 30mA)