Hello,
Doing an install for a standby generator for a customer that has a 400A (320A) meter that feeds 2x200A panels via 2 sets of conductors (the split is at the meter base). The Generator is a Generac and both 200A and 400A transfer switches are available. The 200A's can be put in parallel.
I was wondering what are the pro's / con's of installing either:
#1: 2x200A ATS - The 400/2x200 split will remain at the meter base.
#2: 1x400A ATS - The split will be done in the 400A ATS (it comes with double lugs)
What I'm thinking so far:
Pro's of 2x200A:
- Cheaper (2x$750 vs $2900)
- PoCo will not give me any trouble by changing the wire configuration in their meter
- The meter base is guaranteed to be compatible with this setup (it might not support 1x400A output)
Pro's of 1x400A:
- Less points of failure
- Easier install for the customer to understand
- Better safety in case of cross-wiring circuits inside the house
- No tapping of conductors or replacing factory lugs required (if doing 2x200A have to swap out single lugs with double lugs).
What are your recommendations ? Anything else I'm missing ?
Thanks !
Doing an install for a standby generator for a customer that has a 400A (320A) meter that feeds 2x200A panels via 2 sets of conductors (the split is at the meter base). The Generator is a Generac and both 200A and 400A transfer switches are available. The 200A's can be put in parallel.
I was wondering what are the pro's / con's of installing either:
#1: 2x200A ATS - The 400/2x200 split will remain at the meter base.
#2: 1x400A ATS - The split will be done in the 400A ATS (it comes with double lugs)
What I'm thinking so far:
Pro's of 2x200A:
- Cheaper (2x$750 vs $2900)
- PoCo will not give me any trouble by changing the wire configuration in their meter
- The meter base is guaranteed to be compatible with this setup (it might not support 1x400A output)
Pro's of 1x400A:
- Less points of failure
- Easier install for the customer to understand
- Better safety in case of cross-wiring circuits inside the house
- No tapping of conductors or replacing factory lugs required (if doing 2x200A have to swap out single lugs with double lugs).
What are your recommendations ? Anything else I'm missing ?
Thanks !