3/0, 225A motor feeder???

Electromatic

Senior Member
Location
Virginia
Occupation
Master Electrician
I have an existing pump station that seems to have undersized conductors. The service comes in to a 225A enclosed breaker, over to an ATS, then to a MLO panel. All of the conductors are 3/0Cu. The primary purpose of the system is the two large pump motors and their vacuum pump primers, but given there are also lights and receptacles in the small structure, is there any way the whole service could fall under an Article 430 calculation? It seems to me the 3/0 is undersized for 225A protection unless I'm missing something. Everything has been in place for years, and I can only guess this was just overlooked when inspected.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
is there any way the whole service could fall under an Article 430 calculation?
Yes:

230.90(A) ". . . protection shall be provided by an overcurrent device in series with each ungrounded service conductor that has a rating or setting not higher than the allowable ampacity of the conductor. . . .
Exception No. 1: For motor-starting currents, ratings that comply with 430.52, 430.62, and 430.63 shall be permitted."

Cheers, Wayne
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have an existing pump station that seems to have undersized conductors. The service comes in to a 225A enclosed breaker, over to an ATS, then to a MLO panel. All of the conductors are 3/0Cu. The primary purpose of the system is the two large pump motors and their vacuum pump primers, but given there are also lights and receptacles in the small structure, is there any way the whole service could fall under an Article 430 calculation? It seems to me the 3/0 is undersized for 225A protection unless I'm missing something. Everything has been in place for years, and I can only guess this was just overlooked when inspected.

I suspect the original installer used the 90C column for 3/0 which would have been 225 amps. However, the 75 C column is what should have been used.
 

Electromatic

Senior Member
Location
Virginia
Occupation
Master Electrician
It is Wayne's spotting of 230.90 that allows even the service OCPD to be adjusted according to 430 calculations.
Service Equipment -- Overcurrent Protection
230.90(A) ". . . protection shall be provided by an overcurrent device in series with each ungrounded service conductor that has a rating or setting not higher than the allowable ampacity of the conductor. . . .
Exception No. 1: For motor-starting currents, ratings that comply with 430.52, 430.62, and 430.63 shall be permitted."
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The exception points to rules for BRANCH circuit protection. If that breaker is the ONLY SCPD for this, then yes, it is a branch. If there are other SCPDs in the control panel, then this 225A breaker is a FEEDER and different rules apply. The OP does not state the size of the motors and vacuum pumps or whether they have individual SCPDs and overload relays, or if the lights and receptacles have their own protection. So really, we can’t tell if those exceptions qualify.
 