3/0 awg copper ran through stud.

Status
Not open for further replies.

Andrewp1

New User
Location
California
Occupation
Electrical
Was wondering, what’s the best way and up to code to run 3 conductors that are 3/0 awg copper into stud frame. Im thinking of running 2in liquid tight. Am I able to notch out 2in into the frame for the liquid tight. Or am I able to make a knockout rite in the center of the stud. Thank you, 1 yr in the field there’s still much for me to learn.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
What kind of building/structure is it?
Is it a load bearing wall?
Outside wall?
How many studs do you need to go through?
What are you trying to power?
 

tom baker

First Chief Moderator
Staff member
2” LT will be stiff, hard to bend and keep in place esp when pulling. Can you run emt?
Punching and notching studs is a building code issue.
Not much stud left on a 2x4 wall with a 2 3/4” hole.
Is this for a service?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Even if you could do it for structural reasons, the code would require you to put nail plates on both sides of the stud wherever you drilled a hole for the liquid tight. I think I would be looking for a different way.

For what kind of electrical circuit would you need to be able to run three 3/0 conductors in LT? Most times you are going to need an equipment grounding conductor as well.
 