We are refeeding a 225 amp panel from the existing switch gear. We used #4/0 due to the amperage of the panel. The electrical engineer has told us that #3/0 is acceptable for the panel. Is #3/0 rated to 225 amps?
Mason Schuler said:We are refeeding a 225 amp panel from the existing switch gear. We used #4/0 due to the amperage of the panel. The electrical engineer has told us that #3/0 is acceptable for the panel. Is #3/0 rated to 225 amps?
m73214 said:Darn.......Late Again:roll:
I believe you have to design the conductor feeding a panel/subpanel with the maximum current in mind.wirebender said:Does the rating of the panel have anything to do with it?
Wouldn't the calculated load determine what size wire you use?
If the load is under 200 amps 3/0 would be okay as long as the OCPD was 200A, wouldn't it?
wirebender said:If the load is under 200 amps 3/0 would be okay as long as the OCPD was 200A, wouldn't it?
hardworkingstiff said:I agree. Since the main was 225, the OP did the correct thing by pulling the 4/0.
wirebender said:The OP didn't say anything about a main. Or about the OCPD.
He just said an existing 225A panel. The engineer said 3/0 was good. How do we know the engineer didn't do a load calc?
Is there somewhere in the NEC that says to size conductors by the panel rating?
If so, when I hook up an A/C unit with a 60A A/C disconnect do I need to pull #6 regardless of the load?
wirebender said:The OP didn't say anything about a main. Or about the OCPD.
hardworkingstiff said:I hate it when I missread stuff. My bad, you of course are correct.