Hi.
I'm looking to run 3, 30A circuits (9 conductors) through 1 conduit. I will be using 3 Junction boxes to house the receptacles.
I have 2 questions.
1. How far apart do the junction boxes need to be from each other? Is there a code for this?
2. If i run 10AWG wires rated for 105 deg C with OD of 0.18" through a 1/2" IMC, would this be fine according to the NEC? How about 8AWG with 105 deg C with OD of 0.262" through a 3/4" IMC?
According to the NEC, running 9 conductors through a conduit means that I have to lower the current rating to 70% of the table. If I want 30A circuits, that means that I have to look for a 43A value on the table for the wire size I want to use. According to the table, I can use cables rating at 90 deg C for 40A for a 10AWG. Guess my question is, can I just get higher rated wires to make up that extra 3A?
Thanks,
-Jeff
I'm looking to run 3, 30A circuits (9 conductors) through 1 conduit. I will be using 3 Junction boxes to house the receptacles.
I have 2 questions.
1. How far apart do the junction boxes need to be from each other? Is there a code for this?
2. If i run 10AWG wires rated for 105 deg C with OD of 0.18" through a 1/2" IMC, would this be fine according to the NEC? How about 8AWG with 105 deg C with OD of 0.262" through a 3/4" IMC?
According to the NEC, running 9 conductors through a conduit means that I have to lower the current rating to 70% of the table. If I want 30A circuits, that means that I have to look for a 43A value on the table for the wire size I want to use. According to the table, I can use cables rating at 90 deg C for 40A for a 10AWG. Guess my question is, can I just get higher rated wires to make up that extra 3A?