Is that possible? Can you have a 600v neutral run within same conduit to same equipment? How can you have a 600v cable going to 15kv gear?
Just read it...wow guess you can have a 600v neutral....minimum. ThanksSee 250.184(A)(1). Note that this only applies to a solidily grounded system.
A solidly grounded system has a grounded conductor which is commonly called a neutral. I don't think line to neutral loads are very common on a customer owned medium voltage system there would often be no grounded conductor run to the loads.Is this a neutral or ground? We run bare or insulated grounds. 15kV cable usually has tape shield or concentric neutral built into the cable. I doubt that the 600V wire is a neutral as much as a ground.
Is this a neutral or ground? We run bare or insulated grounds. 15kV cable usually has tape shield or concentric neutral built into the cable. I doubt that the 600V wire is a neutral as much as a ground.