3.7 hp compressor motor no NEC FLA listed

Status
Not open for further replies.

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
When trying to size a feeder/ branch circuit for a 3.7 horsepower, single phase compressor at 230 volts

The NEC does not have a listing for 3.7 hp motor under its table for single phase motors. How then are you to size the feeder to 125% of the motor full load current according to NEC table when such a horsepower isn’t listed?

Or does this fall under appliance rules?
 

Attachments

  • IMG_1995.jpeg
    IMG_1995.jpeg
    74.3 KB · Views: 15
  • IMG_1993.jpeg
    IMG_1993.jpeg
    92.7 KB · Views: 14
Surprised it didn't come cord & plug. The HP rating you see is a sales gimmick...ignore that and follow hbliss's advice
 
You could simply use the tabulated value for a 4 HP motor (if one appears in the table - I don't have my code book handy).
 
It’s interesting that the motor nameplate left the horsepower rating out
Very typical for special purpose motors used for equipment when the manufacturer uses a fictitious horse power for marketing purposes...they use something like peak horsepower or a horsepower calculated from the inrush current. However that does not appear to be the case here with a nameplate current of 15.7 amps and Table 430.148 shows 17 amps for a 3 hp motor at 230 volts. The numbers in the table are very conservative so it is probably possible to build a 3.7hp motor with a full load current of 15.7.
 