Re: 3 and 4 way travelers
310.15(B)(2)(a) Adjustment Factors.
More Than Three Current-Carrying Conductors in a Raceway or Cable. Where the number of current-carrying conductors in a raceway or cable exceeds three, . . .
In the quote I emphasize the active present tense of the adjective used to describe the type of conductor to be counted. The conductor is not the conductor that will, or that has carried current, but
is carrying current.
Supporting this are 310.15(B)(4) and 310.15(B)(5) which describe conductor uses, while present in a raceway, that are not counted for Table 310.15(B)(2)(a) adjustment purposes.
This is aimed at, IMO, ensuring the temperature inside the raceway does not exceed the insulation rating. The current-carry
ing conductor is the one that heats from the I?R and adds to the heat concentrating in the confined space of the raceway, thus resulting in the temperature increase.
Therefore, only one of the 3- and 4-way travellers should be counted.
The one exception to this general statement for travellers that I can think of is that of the 4-wire
Travelling Bus Threeway which has one setting where all four conductors are carrying current simultaneously.
Edit to update the Link to the Travelling Bus - Al
[ March 17, 2005, 09:53 AM: Message edited by: al hildenbrand ]