3 CCC's In raceway

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I constantly see this in the specs. Ridiculous IMO. Are they worried about derating and having more than 3 CCC in a raceway? They say 3 CIRCUITS that would be more than 3 CCC if counting the neutral(s), no? Thanks.
1704312171468.png
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Three circuits, each having their own neutral takes you to an 80% ampacity adjustment.

Maybe a very old spec based on 75°C conductors and a 3-phase multiwire branch circuit, giving you only 3 current carrying conductors. With 75°C conductors, even the 80% ampacity adjustment would require you to increase the conductor size or decrease the OCPD rating.

However, assuming circuits with OCPDs of 30 amps or less, and THHN or other 90°C conductors, there is no issue going up to 9 current carrying conductors.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
However, assuming circuits with OCPDs of 30 amps or less, and THHN or other 90°C conductors, there is no issue going up to 9 current carrying conductors.
Not quite; a common misconception. For a 30 amp circuit with #10 THHN conductors, the limit is 6 CCCs, not 9.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Three circuits, each having their own neutral takes you to an 80% ampacity adjustment.

Maybe a very old spec based on 75°C conductors and a 3-phase multiwire branch circuit, giving you only 3 current carrying conductors. With 75°C conductors, even the 80% ampacity adjustment would require you to increase the conductor size or decrease the OCPD rating.

However, assuming circuits with OCPDs of 30 amps or less, and THHN or other 90°C conductors, there is no issue going up to 9 current carrying conductors.
A 3 phase MWBC would require a neutral, that would be 4 ccc, no?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
That's correct for 4-6 CCC's (80%). 7-9 CCCs (70%) drops you below 30 amps.
That is why I remember that the "limit" for 30 amp circuits with #10 THHN is 6 CCCs, whereas it is 9 CCCs for 20 amp circuits with #12 THHN.
 