Yes if there are separate neutrals that would be 6 CCC's for 3 circuits.They say 3 CIRCUITS that would be more than 3 CCC if counting the neutral(s), no? Thanks.
Not quite; a common misconception. For a 30 amp circuit with #10 THHN conductors, the limit is 6 CCCs, not 9.However, assuming circuits with OCPDs of 30 amps or less, and THHN or other 90°C conductors, there is no issue going up to 9 current carrying conductors.
240.4(B) would permit the 30 amp OCPD unless the circuit supplies multiple receptacles.Not quite; a common misconception. For a 30 amp circuit with #10 THHN conductors, the limit is 6 CCCs, not 9.
A 3 phase MWBC would require a neutral, that would be 4 ccc, no?Three circuits, each having their own neutral takes you to an 80% ampacity adjustment.
Maybe a very old spec based on 75°C conductors and a 3-phase multiwire branch circuit, giving you only 3 current carrying conductors. With 75°C conductors, even the 80% ampacity adjustment would require you to increase the conductor size or decrease the OCPD rating.
However, assuming circuits with OCPDs of 30 amps or less, and THHN or other 90°C conductors, there is no issue going up to 9 current carrying conductors.
No. Unless more that 50% of the load were non-linear (highly unlikely) the neutral in a 4 wire MWBC from a 3 phase Wye system would not be counted as a CCC.A 3 phase MWBC would require a neutral, that would be 4 ccc, no?
Derating #10's. 90 degree column #10 good for 40A? 80% of 40A = 32A.Not quite; a common misconception. For a 30 amp circuit with #10 THHN conductors, the limit is 6 CCCs, not 9.
That's correct for 4-6 CCC's (80%). 7-9 CCCs (70%) drops you below 30 amps.Derating #10's. 90 degree column #10 good for 40A? 80% of 40A = 32A.
That is why I remember that the "limit" for 30 amp circuits with #10 THHN is 6 CCCs, whereas it is 9 CCCs for 20 amp circuits with #12 THHN.That's correct for 4-6 CCC's (80%). 7-9 CCCs (70%) drops you below 30 amps.