treyp3
Member
- Location
- Fernandina Beach Fl
Is there a rule, and if so where, that says I cant have 3 circuits in one box? I want to hang a 2 gang nail on box in a kitchen. I want to use it for switch and receptacle. I want to use a 14-3 conductor (two pole 15 amp breaker) home run for dish and disposal, and a 12-2 kitchen appliance circuit. So I will have a 3 wire feeding a switch leg for the disposal and a hot for the dish washer. Also, I'd have a 12-2 wire for the kitch. app.The wire fill is 29.75 cu. in. and the box is 32 cu. in. I've been told this isn't legal, but I don't know where to look it up.