When calculating 3-phase max available short circuit current at transformer secondary, considering 3 individual transformers.
This is best asked with a simple example:
Primary Service: 4160V 3P 3W
Three (3) individual cans each: 100kVA; 2400:277; Z=2%; Connected D-Y.
Secondary Service: 480V 3P 4W
.
Max Avail Fault Amps= (300kVA)/(480*SQRT(3)*(.02*2))=9,021 Amps
OR
Max Avail Fault Amps=(100kVA)/(277V*.02)=18,050 Amps
.
Which is correct? Thanks