There is no single "right" answer. If this is a test question, then it is an unfair test question. Everything depends on why you are doing the calculation, and what you intend to do with the results. Averaging the three currents will give you the more reasonable representation of the total load on the system. I would use this value if I were giving the mechanical engineers information for them to use in estimating the performance of their ventilation system. Taking the highest current (the conservative or "worst case" value) will give you a better answer, if you are trying to decide whether there is capacity for adding load to the system.
Which is right:Am I missing something. 120/208V would be a Wye connected load. The total KVA is just the sum of the three phase currents times the L-N voltage of 120V (assuming a PF of 1.0).
Pretend you will do it first. The answer you get will be the 20KVA unit. I see no reason that is not sufficient. But the final decision might be based on the likelihood that future growth might make the 20 KVA unit too small.I know the load needs to be balanced, but that will come later.
Charlie,
Am I missing something. 120/208V would be a Wye connected load. The total KVA is just the sum of the three phase currents times the L-N voltage of 120V (assuming a PF of 1.0).
Mark
go with the bigger ups.Not a test question.
I am sizing a UPS for this system and was trying to determine the existing kVA on the panel.
I know the load needs to be balanced, but that will come later.
I used the highest current for my calculation.
If I average the current I get ~10kVA. If I use the highest current I get ~14kVA.
Along with the existing load and the future capacity requested it is the difference between a 20 and 30 kVA UPS.