Assuming that I am using
- Fuse RK5 with 400A = Fuse1
- Circuit Breaker with 200A and 65kA interrupt rating = CB1
- Circuit Breaker with 100A and 65kA interrupt rating = CB2
I need to establish a series rated system starting at the fuse1 and than connected downstream first the breaker CB1 for section 1 and than second CB2 as branch outlet. Of course Section Breaker CB1 will have several parallel breakers as well as the CB2.
I do have series rated documents for Fuse1 to CB1 and Fuse 1 to CB2, which are showing that both breakers individually are series rated with the fuse for up to 150kA@480V.
Would an AHJ or Inspector allow me to use this individual series rated reports to establish this a.m. 3-level series rated system?
Or do we have to do a series rating test with official report for exact this 3 level arrangement.
I do also know that I have to observe the motor contribution if available.
Thanks
Gustav
- Fuse RK5 with 400A = Fuse1
- Circuit Breaker with 200A and 65kA interrupt rating = CB1
- Circuit Breaker with 100A and 65kA interrupt rating = CB2
I need to establish a series rated system starting at the fuse1 and than connected downstream first the breaker CB1 for section 1 and than second CB2 as branch outlet. Of course Section Breaker CB1 will have several parallel breakers as well as the CB2.
I do have series rated documents for Fuse1 to CB1 and Fuse 1 to CB2, which are showing that both breakers individually are series rated with the fuse for up to 150kA@480V.
Would an AHJ or Inspector allow me to use this individual series rated reports to establish this a.m. 3-level series rated system?
Or do we have to do a series rating test with official report for exact this 3 level arrangement.
I do also know that I have to observe the motor contribution if available.
Thanks
Gustav