3? Load Calculator

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
3Oslashloadcalculator.gif
 

Smart $

Esteemed Member
Location
Ohio
Being just out of the blocks, I ask users to scrutinize the results. With all the formulas and considerations involved, it is not inconceivable that there may be errors... :happyno:
 

Smart $

Esteemed Member
Location
Ohio
BTW, it's not just for 208/120. Also can select 480/277 on the WYE tab. A second tab (worksheet) covers 240/120 and 480/240 delta high leg. If one is careful, can also be used for 120/208 and 120/240 1?.
 

Besoeker

Senior Member
Location
UK

Smart $

Esteemed Member
Location
Ohio
Both worked however I can't figure out how to input data

I was thinking of the old question about a 3 phase panel with single phase 208 loads

3- single phase loads at 4500 watts for instance
On three separate lines enter in the AMPERES column "=4500/120/sqrt(3)" without quotes (NOTE: you could enter "=4500/208", but it will give some rounding error because I use the technical value of 120*sqrt(3) for the calculations).

Then assign AB, BC, and CA (in any order) to the lines in CONNECTION column (cells use Data Validation; click cell, click drop arrow, select CONNECTION).

Also assign a PF of 1 to each.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Thanks Smart- that worked. One issue I saw is it would not let me enter ab, bc, ac and I to change the ac to ca but all is good .. Thanks
 

Smart $

Esteemed Member
Location
Ohio
Thanks Smart- that worked. One issue I saw is it would not let me enter ab, bc, ac and I to change the ac to ca but all is good .. Thanks

I just figured to use neutral calcs you type AN. You need instructions for some of us..:D
The calculations rely on specific entries (e.g. CA vs. AC). That's why I used Data Validation for those entries. Drop box is a clue when those cells are selected. PF also uses Data Validation (values must be from -1.00 to +1.00) but no drop box. I enabled Error message for it, but not the others.

Write up instructions??? Not me! At least not comprehensive instructions. I'll provide bit-by-bit instructions, as needed, in my postings.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The calculations rely on specific entries (e.g. CA vs. AC). That's why I used Data Validation for those entries. Drop box is a clue when those cells are selected. PF also uses Data Validation (values must be from -1.00 to +1.00) but no drop box. I enabled Error message for it, but not the others.

Write up instructions??? Not me! At least not comprehensive instructions. I'll provide bit-by-bit instructions, as needed, in my postings.

Thank you- I was not serious about writing instructions. With your help here there is no need. Thanks
 

Smart $

Esteemed Member
Location
Ohio
I'm now thinking there is another [major] error in the vector calculation. Watching NFC Championship right now... will get to it later and verify.
 

Smart $

Esteemed Member
Location
Ohio
I'm now thinking there is another [major] error in the vector calculation. Watching NFC Championship right now... will get to it later and verify.
Unbelievable finish!!!

Anyway, on the error I mentioned, I'm now thinking I messed up on the pf shift. I usually use a different angle convention for my calculations. I based this calculator on a previous one I developed for another member here, using the opposite direction. In my normal method I subtract the power factor angle... and in this calculator I should have added. At least this is what I'm thinking. I will verify, revise, and post if my thinking is correct....
 