I have 3 small HP motors.
A 1hp, and two .75hp.
Here is what I came up with.
largest FLC, 2.1x125%=2.6
Plus the sum of other two,1.6+1.6=3.2
Total, 2.6+3.2=5.8
Could use #14THHN but had #12 handy so will be using it.
But where I am getting hung up is sizing SC/GF protection. Each motor has its own starter with overloads.
But for the SC/GF Do I just use
430.53 (C)(4). Some info I forgot to add 480v 3ph squirrel cage.
So do I just take my Total added FLC of 5.8x250%=14.5 and use a 15ampere OCPD. Or am I still permitted to use 20amp OCPD since I used #12?
sorry I am having a brain fart……
A 1hp, and two .75hp.
Here is what I came up with.
largest FLC, 2.1x125%=2.6
Plus the sum of other two,1.6+1.6=3.2
Total, 2.6+3.2=5.8
Could use #14THHN but had #12 handy so will be using it.
But where I am getting hung up is sizing SC/GF protection. Each motor has its own starter with overloads.
But for the SC/GF Do I just use
430.53 (C)(4). Some info I forgot to add 480v 3ph squirrel cage.
So do I just take my Total added FLC of 5.8x250%=14.5 and use a 15ampere OCPD. Or am I still permitted to use 20amp OCPD since I used #12?
sorry I am having a brain fart……