Gentlemen (and ladies). I have a best practices question that I humbly request an expert opinion on.
600 amp 3 phase 208Y/120 service. Comes into a CT Cabinet and then I want to distribute it to various breakers, mostly single phase 20 amp but a few 3 phase 40 amp.
My contractor thinks 3 separate 200 amp breakers is the way to go. I think 1 600 amp panel is easier, although possibly more expensive. Code is not clear to me and I wanted an outside opinion. The service feeders are a single set of wires. It seems like more work and unneeded redundancy to have 3 separate main breakers rather than a single 600 amp breaker.
I can follow his logic but I don't know why in an emergency, needing to turn off three separate panels to turn power off is considered permissible, even if they are situated in the same area. There has been no talk of a main disconnect.
600 amp 3 phase 208Y/120 service. Comes into a CT Cabinet and then I want to distribute it to various breakers, mostly single phase 20 amp but a few 3 phase 40 amp.
My contractor thinks 3 separate 200 amp breakers is the way to go. I think 1 600 amp panel is easier, although possibly more expensive. Code is not clear to me and I wanted an outside opinion. The service feeders are a single set of wires. It seems like more work and unneeded redundancy to have 3 separate main breakers rather than a single 600 amp breaker.