Good advice.Make sure you have the correct breaker per 240.85: A slash rated breaker is not designed to interrupt L-L voltage with a single pole.
Also remember if you pick the grounded phase then all the rules of article 200 and 240.22 apply: Really common to find misidentified and fused grounded conductors on corner deltas.
THE service is fed from PO to a two pole disconnect hot legs fused. grounded leg Is not and bonded to the disconnect .then goes to 3 phase panel with three phase 200 amp main breaker. so I will be ok to use any two legs for my two pole 240 volt single phase AC ?
Make sure you have the correct breaker per 240.85: A slash rated breaker is not designed to interrupt L-L voltage with a single pole.
Also remember if you pick the grounded phase then all the rules of article 200 and 240.22 apply: Really common to find misidentified and fused grounded conductors on corner deltas.
The other thing I would say is that, while this is often overlooked, all devices, panelboards, etc. must be rated for use on a corner grounded system.
I've always thought it fell under 408.58 and 110.3(B)... but every time I bring it up, others say in essence, it is not so. :blink:Do you have a code section to look at?
I've always thought it fell under 408.58 and 110.3(B)... but every time I bring it up, others say in essence, it is not so. :blink:
You are correct.
In fact, UL has 'special' listing requirements for corner-grounded equipment.
Don't forget to also quote 240.85.
And the grounded conductor is covered by all of the rules, including the identification rules, found in Article 200. I don't think I have every seen a grounded phase system that complied with those rules.
The issue is usually not the panel, if a 3-phase version is available like with QO load centers, but the common 2 pole breakers are almost always a concern.I always thought the reason for this was to prevent, say, a person from using a 120/240 garden variety "load center" on a 240 volt corner grounded system that is not rated for 240 volts to ground.
There may be another caveat I'm missing, but I believe the intent of that section is to be sure that no single breaker pole is opening a voltage higher than it is designed for, the same as how you can't use a slash-rated breaker on a high leg delta.I would agree but I might add that this would be OK for the 1 phase equipment in the OP's case. If he was going to supply a 3 phase load with a 2 pole breaker, then a breaker marked 1 phase-3 phase would be required...