I looked at a commercial installation with the following. 800 Amp 3P4W distribution board(not service equipment) 1-switch feeds a 3p 4W panel fused at 100Amps. The nuetral in this panel is feed with #8 wire and the feeds are # 2THHN.
The load is only 6 cirts. all 120V low amps.
Is this a code violation?
If I increase the neutral to a # 3 THHN would this meet code ? Since feeds are # 2THHN. #3 for the neutral since its rated for 100amps and the panel is fused at 100Amps. Thanks
The load is only 6 cirts. all 120V low amps.
Is this a code violation?
If I increase the neutral to a # 3 THHN would this meet code ? Since feeds are # 2THHN. #3 for the neutral since its rated for 100amps and the panel is fused at 100Amps. Thanks