Hi Gentlemen,
I would like to consult with the forum on what is the proper voltage (120v or 208v) to be used in a voltage drop calculation for the main feeder (4 wire) supplying a 3 phase/main lug/42 single breakers panel.
Please help. Thank you
You could do either. There will be a factor in the numerator that will depend on which voltage you use.
Short answer:
Using 208V phase-to-phase voltage, there is a sqrt(3) factor in the numerator, in place of the 2 you use for single phase and DC.
Using 120V phase-to-neutral voltage, this factor in the numerator will drop out of the equation. The 2 that is there for single phase and DC becomes a 1.
To understand why, I think about in terms of "effective round trip length". For single phase 2-wire and DC 2-wire, it is the length along the circuit from the source to the load and back to the source. Twice the one way length (suppose 100 ft). Current travels 100 ft on the black wire, and 100 ft back on the white wire.
For three phase circuits, the effective round trip length is significantly less. And this is due to the fact that phases B and C, will be carrying the return current, while phase A is delivering the current to the load. Current only needs to travel out on phase A, and it will not create additional voltage drop on phases B and C. Phases B and C, already carry the return current of phase A's current when they carry the cycle of their own current, without imposing heating due to phase A current on any conductor other than phase A.
Using the phase-to-neutral voltage, the "effective round trip length", is the one-way length. Because the remaining two phases carry return current, which coincides with what they are already carrying.
Because the phase-to-phase voltage = sqrt(3)*phase-to-neutral voltage, we multiply by 1 in a fancy way, to make a formula that works for the phase-to-phase voltage. Multiply by sqrt(3)/sqrt(3), and replace (sqrt(3)*Vpn) with Vpp. The other sqrt(3) remains upstairs in the numerator. The effective round trip length is sqrt(3)*one-way-length, when using phase-to-phase voltage.
For split phase 3-wire systems carrying a balanced load, you can think of it as two opposite phase 120V sources sending current over an effective round trip length equal to the one-way-length. Or you can think of it as 240V sending current out on the black wire, and returning on the red wire, a round trip length equal to twice the one-way length. Either way, they give the same answer.