wire monk said:The transformer feeding the building is 3 phase 3 wire 120/208 and we want to put 4 meters on the building single phase 2 wire 120/
208 single phase 2 wire to each meter can it be done??
Yes, and I've done it. (It will be four wires, like the guys said.) The voltage in each panel will be 120/208, not 120/240. so make sure all "220v" loads are rated for 208v also.wire monk said:The transformer feeding the building is 3 phase 3 wire 120/208 and we want to put 4 meters on the building single phase 2 wire 120/
208 single phase 2 wire to each meter can it be done??