I do mostly residential work; and therefore, I rarely work on 3 phase circuits. However, I have a customer who needs a forklift charger installed for a single lift that is rarely used in a small factory. The max amp rating on the nameplate of the charger is 25 amps at 208v/3 phase.
I was planning on running #10 from a 3 pole 30A breaker in the panel to a 30A twist lock receptacle right next to the panel in EMT. Then run a 10/4 SOOW about 8 feet from the receptacle to the charger. This is a charger not a motor, so no need to figure 135% for continuous load?
Apparently 10/3 SOOW is rated for 30 amps but 10/4 rated only for 25. Perhaps use 8/4 SOOW instead?
We are on 2008 NEC here. I don't see how this could be wrong, but just wanted to be sure.
I was planning on running #10 from a 3 pole 30A breaker in the panel to a 30A twist lock receptacle right next to the panel in EMT. Then run a 10/4 SOOW about 8 feet from the receptacle to the charger. This is a charger not a motor, so no need to figure 135% for continuous load?
Apparently 10/3 SOOW is rated for 30 amps but 10/4 rated only for 25. Perhaps use 8/4 SOOW instead?
We are on 2008 NEC here. I don't see how this could be wrong, but just wanted to be sure.