Power company recently replaced transformers and now that businesses are opening back up.
Customer had lost some lights. This is a 277/480 volt system.
Measured voltage on tenant panel 480 A-B, A-C, B-C.
But read 480 A to N, 0 B to N, 480 C to N. (Read the same voltage measured to Ground)
Went to electrical room, couldn’t really get into main ( no AF gear) but did remove one dead front and 4 - 200 amp breakers all read the same as the aforementioned tenant panel ( but I read to Ground as Neutral wasn’t safely accessible, but neutral SHOULD be bonded at main... ).
120 volt lighting and receptacles seem to work, the mall is 95% closed, so it’s not possible to enter all tenants, and no complaints been made yet but the one. 120 seem to all be working in tenant I visited ( couldn’t check everything, overly inventoried dress store, just checked panels). And honestly with 480 not reading proper I did not look too much down stream.
Supposedly Ga Power changed the transformers ( underground vault , blew up) two days before the corona shut down order. Word is the tenants had no issues but the one I initially investigated, yet I find this voltage anomaly on 6 or 7 disconnects in the electrical room. The main switchboard feeds straight underground maybe 50’-75’ to the utility transformer vault.
Thoughts? Reminds me of the 240 open Deltas we have in industrial parks around here. Is this a faulted/open situation effectively creating an open Wye? I’ve lost phases before ( fuses, breakers, burnt wires) but what buffalos me here is where’d the neutral go?
Customer had lost some lights. This is a 277/480 volt system.
Measured voltage on tenant panel 480 A-B, A-C, B-C.
But read 480 A to N, 0 B to N, 480 C to N. (Read the same voltage measured to Ground)
Went to electrical room, couldn’t really get into main ( no AF gear) but did remove one dead front and 4 - 200 amp breakers all read the same as the aforementioned tenant panel ( but I read to Ground as Neutral wasn’t safely accessible, but neutral SHOULD be bonded at main... ).
120 volt lighting and receptacles seem to work, the mall is 95% closed, so it’s not possible to enter all tenants, and no complaints been made yet but the one. 120 seem to all be working in tenant I visited ( couldn’t check everything, overly inventoried dress store, just checked panels). And honestly with 480 not reading proper I did not look too much down stream.
Supposedly Ga Power changed the transformers ( underground vault , blew up) two days before the corona shut down order. Word is the tenants had no issues but the one I initially investigated, yet I find this voltage anomaly on 6 or 7 disconnects in the electrical room. The main switchboard feeds straight underground maybe 50’-75’ to the utility transformer vault.
Thoughts? Reminds me of the 240 open Deltas we have in industrial parks around here. Is this a faulted/open situation effectively creating an open Wye? I’ve lost phases before ( fuses, breakers, burnt wires) but what buffalos me here is where’d the neutral go?