We have been asked to install a 250 kW emergency generator set on an existing 200 Amp service. The service is a 3-phase 3-wire 480V 200 Amp service from three customer owned individual 37.5 kVA step-down transformer pots (13.2kV-480V). The transformer primaries and secondaries are wired in delta-delta. The frame of the transformer pots are bonded to the metal gate and fencing enclosing the transformers, the metal conduit enclosing the service entrance conductors and connected to a driven rod. There is no apparent connection from the transformer windings to the conduit/ground rod.
There are two delta-wye step down transformers inside the building.
My questions are as follows:
1) When we took voltage measurements with a high impedance digital multimeter, we obtained the following readings: Phase-to-Phase on all three legs = approximately 480 Volts evenly balanced. When we took phase to the metal conduit voltage readings the values were 205, 295 and 260 Volts. How are we able to obtain voltage to ground readings even though the conduit/ground system is isolated from the transformer windings? If this is a phantom voltage, what method could be used to verify that the system is indeed isolated?
2) According to the NEC what are my responsibilities as the installing contractor with regard to the existing service? I know a new service at the potential needs to be grounded, but I am not directly touching the existing service.
3) What are the safety concerns if the existing system is left as is?
Thanks for all replies.
Stu
There are two delta-wye step down transformers inside the building.
My questions are as follows:
1) When we took voltage measurements with a high impedance digital multimeter, we obtained the following readings: Phase-to-Phase on all three legs = approximately 480 Volts evenly balanced. When we took phase to the metal conduit voltage readings the values were 205, 295 and 260 Volts. How are we able to obtain voltage to ground readings even though the conduit/ground system is isolated from the transformer windings? If this is a phantom voltage, what method could be used to verify that the system is indeed isolated?
2) According to the NEC what are my responsibilities as the installing contractor with regard to the existing service? I know a new service at the potential needs to be grounded, but I am not directly touching the existing service.
3) What are the safety concerns if the existing system is left as is?
Thanks for all replies.
Stu