No that is not normal. Did you open the MSB to see what's inside?So the neutral wire from the panel is bonded to the MSB can? Is this common with older gear?
It's pretty normal in my experience. Federal pacific seems to have been common when neutrals and grounds were intermingled all over the place.No that is not normal. Did you open the MSB to see what's inside?
Bonding a feeder neutral to the 3Ø, 3-wire main switchboard enclosure is normal?It's pretty normal in my experience. Federal pacific seems to have been common when neutrals and grounds were intermingled all over the place.
Someplace, somewhere the center point of the 208 is bonded or earthed. Hopefully they aren’t using building steel or conduit as the neutral return path, but it wouldn’t be the first time. I would think your line to neutral voltages would be all over the place if it was only a rod.I should clarify, it is a 1600A., 208v, 3ph., 3w. switchboard downstream of the Main 480v. Switchboard at a huge shopping mall. But there are 208/120v. panelboards being fed out of this switchboard so where is the neutral coming from? A field installed neutral bar sounds plausible - and that is connected to a ground rod? I will just have to go look. Thanks for all the comments.
I've seen it many times, mostly in older facilities (maybe 1980s construction and older).Bonding a feeder neutral to the 3Ø, 3-wire main switchboard enclosure is normal?
With the enclosure and metal raceways carrying the neutral beyond there or just an improper bond of the grounded conductor?I've seen it many times, mostly in older facilities (maybe 1980s construction and older).
Improper bonding. In my experience it is not uncommon to see grounds and neutrals freely intermingled in older facilities. I would say it is most common in commercial type structures.With the enclosure and metal raceways carrying the neutral beyond there or just an improper bond of the grounded conductor?
I notice a fair amount of that kind of thing from that time period as well.Improper bonding. In my experience it is not uncommon to see grounds and neutrals freely intermingled in older facilities. I would say it is most common in commercial type structures.