in what kind of applications would you use this transformer set-up? What is
that high leg good for?
that high leg good for?
augie47 said:(every time I post, I step on someone,...slow typer...sorry Trevor...)
Cody K said:What is the difference in powering a motor for instance using the the high leg 208 on this system and using the 208 on 208Y/120 system. I know the first is a line to neutral load and the last is line to line. Will the load operate differently? Augie is that what you were refering to with reduced neutral capacity?
augie47 said:Cody,
In regard to the "reduced neutral capacity", someone who understands transformer windings could enlighten us, but every 240 3 phase transformer I've seen (that has a 120v tap) has a warning that the neutral load can not exceed 5% (I think thats the number) of the transformers KVA capacity. It has to do with the windings.