Hello all
I run the maintenance shop at a senior living facility. Our feed from the road to our building is supplied by NYSEG. For the past few weeks I had several electrical motors/VFD'S/ Contactors and Ballasts go bad. Not new by any means but then my elevator stopped running due to low voltage too drive. So I started going around the building checking legs on panels and all 3 legs are low. I went to our main connect that is 20ft from Transformer on pad . I got on leg 1 262v to N Leg 2 264v to N and leg 3 263v to N. This is while under load on a 480/277 service. My question is what is the allowable voltage drop from the supplier to our connection. In any other building I have been in each Leg was very close to 277 as it should be and 480 leg to leg at over 100ft from transformer. I had the power company out and they agreed voltage was low and that they are going to bump sub station but this morning still lower then I would like to see. It is better then yesterday I was getting like 256v on the legs. I cannot find anyplace what the acceptable power should be from the supply with this type of service. should it be 480/277 + or - a volt or two or does it fall under the 5% / 3% rule. Any info would be greatly appreciated.
I run the maintenance shop at a senior living facility. Our feed from the road to our building is supplied by NYSEG. For the past few weeks I had several electrical motors/VFD'S/ Contactors and Ballasts go bad. Not new by any means but then my elevator stopped running due to low voltage too drive. So I started going around the building checking legs on panels and all 3 legs are low. I went to our main connect that is 20ft from Transformer on pad . I got on leg 1 262v to N Leg 2 264v to N and leg 3 263v to N. This is while under load on a 480/277 service. My question is what is the allowable voltage drop from the supplier to our connection. In any other building I have been in each Leg was very close to 277 as it should be and 480 leg to leg at over 100ft from transformer. I had the power company out and they agreed voltage was low and that they are going to bump sub station but this morning still lower then I would like to see. It is better then yesterday I was getting like 256v on the legs. I cannot find anyplace what the acceptable power should be from the supply with this type of service. should it be 480/277 + or - a volt or two or does it fall under the 5% / 3% rule. Any info would be greatly appreciated.