R Rlmwireman Member Location Evart, MI Occupation Electrician Jan 31, 2020 #1 I gonna run 2 sets 3/0copper what size ground in each set
T texie Senior Member Location Fort Collins, Colorado Occupation Electrician, Contractor, Inspector Jan 31, 2020 #2 See 250.122. It must full size in each raceway.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jan 31, 2020 #3 Each is sized as if it was the only one.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jan 31, 2020 #4 Assuming this is a feeder then texie gave you the correct answer. If these are SEC's then there are no EGC's.