Darick
New User
- Location
- Oak Park, MI
- Occupation
- Electrical Controls Engineer
The company I work for is supplying an MCC for various equipment. One of the pieces of equipment is a 100KW, 3 phase, 460V immersion heater (tank or Vessel heater) with an FLA of 126 Amps. The MCC bucket provided for the heater comes with an On/Off contactor, a 250 Amp Breaker and a Current sensing device that allows the PLC to monitor the branch circuit current and turn the contactor off if the current rises to an alarm level. I am referencing article 427.57 for the MOCP and it turns me back to article 210.3 and 210.23. I cannot find anything that tells me the Max overcurrent protection rating for the heater... only that the branch circuit must be sized for the overcurrent device. I have two questions, 1.) Is there a MOCP rating for a Vessel Heater and 2.) can a branch circuit be sized to the current limit set in the PLC, that controls the on/off contactor?