3 Phase grounded delta three wire 480 volt to single phase 240/120 volt transformer to 200 amp panel , does the 480 volt grounded phase always come in contact with the neutral of the 200 amp panel through bonding ?
 

kwired

Electron manager
Location
NE Nebraska
And that 480 volt system grounded conductor is in contact with the grounded conductor of the source supplying it - from POCO's is often a system that is 7200 volts to ground.
 

domnic

Senior Member
Occupation
Electrical Contractor
Grounded phase

Grounded phase

No matter witch two of the 3 phase transformer lugs I use the grounded phase will be in contact with the neutral in the 120/240 panel.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
No matter witch two of the 3 phase transformer lugs I use the grounded phase will be in contact with the neutral in the 120/240 panel.
Well, OK, but since the primary and secondary are only connected magnetically it doesn't make any difference. You could, for example, feed 480V corner grounded to the primary and have 208/120Y on the secondary with the center of the wye grounded.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No matter witch two of the 3 phase transformer lugs I use the grounded phase will be in contact with the neutral in the 120/240 panel.

The corner ground has a single grounded phase what if you use the two ungrounded phases?
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
The corner ground has a single grounded phase what if you use the two ungrounded phases?
It doesn't matter. The transformer secondary doesn't know or care if one of the primary phases is grounded. Grounding is a DC quantity and transformers do not pass DC.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I agree



I am puzzled.
Ground is an offset of zero volts DC and as such is not passed by a transformer. That may not be mathematically rigorous but it gets the point across. To me, anyway. :D
 