Bburdette
Member
- Location
- Aberdeen, SD
We are changing out an existing Chiller that has 2 480v feeders running to it. One is 500a breaker w/ parallel 350kcm xhhw-2 and the other is 250a breaker w/ 350kcm xhhw-2. The new unit calls for a 500a circuit breaker at 416a load and a 350a circuit breaker at 224a load. Distance is 316ft to the disconnecting means. We need to change out the cable on the new 350a circuit, I had calculated it out at 500kcm xhhw-2. My struggle is calculating the 500a circuit. The HVAC contractor assumes that because it is already 500a breaker the cable should be adiquit but when I run the caluculations for the existing parallel 350kcm and its not coming out large enough to handle the new load. Thoughts? What am i missing?