3 Phase 480VAC Emergency Generator Cable installation?

Status
Not open for further replies.
I don't see a problem there but what about 300.3(B)(1) . The exception does not seem to apply here because the raceway does not appear to be plastic. Sorry I show my ignorance here but it doesn't look correct to me
 
I think you have to run all the circuit conductors together in the same pipe.

I don't think the "crossing" is an issue.

Looks like a very small bonding wire.
 
I don't see a problem there but what about 300.3(B)(1) . The exception does not seem to apply here because the raceway does not appear to be plastic. Sorry I show my ignorance here but it doesn't look correct to me

Little hard to tell for sure from the photo, but this looks like an MI cable install and it looks like there is a non-ferrous mounting plate for the cables. Looks OK from here. I will say that those bonding jumpers look light as compared to the cable size, but that is just a guess from what I see in the photo.
 
Not good in my book

Not good in my book

Think eddy currants you have a problem if there is any steel between phases.
 